Forum-Gallery-Shop-Sponsors

« Advertise on Freel2.com

Home > Off Topic > Any electricians on here ?
Post Reply  Down to end
Page 1 of 2 12>
Print this entire topic · 
jules



Member Since: 13 Dec 2007
Location: The Wilds of Warwickshire
Posts: 4998

United Kingdom 2014 Freelander 2 SD4 SE Auto Firenze Red
Any electricians on here ?

Im pretty good at sorting my domestic electrics but this has got me stumped.

My Consumer Unit has 13 MCBs in 2 banks (bank 1 and bank 2) each with a RCD.

For the last two weeks I've been getting seemingly random trips of Bank 1 RCD.
No MCBs have tripped.

It suddenly got much worse three days ago with RCD 1 tripping 5 to 10 times a day - never at night.

Ive tried my hardest to discover which circuits are causing the RCD 1 trips. But it seems very random.

What is even more puzzling to me is that I can sometimes trigger a RCD 1 trip by switching on something that is on the Bank 2 circuit (eg a light switch or cooker or microwave. But it doesnt happen every time.
More often RCD 1 has tripped when nothing was switched on or off, as far as I can tell.

It was suggested that the freezers might be causing it as they are all on different circuits on Bank 1. So I moved all three freezers onto Bank 2 with extension leads. RCD2 has not tripped but RCD 1 still trips at odd times though not as frequently today as yesterday.

I wondered if it was a dodgy RCD unit as it tripped twice when I let the metal door of the CU close abruptly (RCD 2 didnt trip) so I changed it for a new one. No improvement.

We're away next week and I have arranged for an electrician to vist when we get back at the end of the month.

Anyone got a suggestion as to how switching something on Bank 2 can cause Bank RCD 1 to trip but not its own RCD 2?

Of note: The CU was installed and certified 2.5 years ago. No new electrics have been installed since then apart from Eon adding a smart meter about 6 months ago, in anticipation of them installing solar panels.

(After a 3 month wait Eon then said they couldnt install the panels as it was too difficult to place the scaffolding around my roof). Jules

Post #445503 19th Oct 2024 3:25 pm
View user's profile Send private message View poster's gallery Reply with quote
Dartman the one



Member Since: 04 Apr 2013
Location: Seville, Spain
Posts: 1687

England 

I know it seems stupid but over the years the cables into each MCCB can become loose mainly due to to them settling due to temperature changes, I suggest you check all the wires from the MCCB's and check the live comb to the MCCB's my PC is slightly to the right of Genghis
2012 HSE SD4 In Orkney Grey now gone, best car ever.

Post #445507 19th Oct 2024 7:39 pm
View user's profile Send private message View poster's gallery Reply with quote
jules



Member Since: 13 Dec 2007
Location: The Wilds of Warwickshire
Posts: 4998

United Kingdom 2014 Freelander 2 SD4 SE Auto Firenze Red

yeah - have done that when I changed the RCD.

Checked all sockets in the house with a 3 light tester.

Had all the sockets out and checked all connections for tightness.



Now I think about it , we've had a lot of rain since Wednesday and that is when the tripping started to get really bad - roads and field flooded. But now its drying up, and now the tripping is getting less frequent as today has passed.

Tomorrow Im going to check the connections from the main fuse and in and out of the smart meter, as these issues are after its installation but by several months. Its on the wall at the back of the house - never gets the sun on it.
Its interesting that the tripping never occurs at night, only during the day - could it be temperature or humidity related ?

My internet research indicates that smart meter installations can sometimes be well below standard; with loose or even reversed connections. Jules

Post #445508 19th Oct 2024 8:28 pm
View user's profile Send private message View poster's gallery Reply with quote
IanMetro



Member Since: 11 Sep 2017
Location: Somerset BS21
Posts: 3126

United Kingdom 2014 Freelander 2 SD4 Metropolis LE Auto Fuji White

I have had, in the past, circuits external to my house trip RCDs.

Mostly I have traced the problem by isolating various sub-feeds, it normally turns out to be water (rain) getting into either external lights or their junction boxes or switches.

Only once did it turn out to be rodent damage (normal mains cable buried in pipe to pond pump - seemed to be an ideal home for suspected Rat), Cables have since been replaced by armoured cables.

Have you outside electricity circuits, and can you isolate them?

As you know the RCD measures differences between the Live and Neutral currents, and therefore will trip if either finds a path to Earth.

Another possible cause (but not likely in domestic setting) is if 3-Phase is involved and heavy industrial machinery starting drags the Neutral-Point away from Earth.

PS thinking about it further
Could it be to do with your heating? A pump or similar would not be called overnight.
OR
Is it a rodent that has moved into your house and believes in a good nights sleep, only nibbling now and again, during the day, FL2 XS SD4 Auto 2010 2012-2017 (21k - 91k miles) (MY2011)
FL2 Metropolis SD4 Auto 2014 2017- (16k - 77k+ miles) (MY2015)
Metro in its 11th Year of (Extended) LR Warranty / Full LR Service History
(Expensive, but Trouble/Worry free - hopefully?)

Post #445511 19th Oct 2024 10:29 pm
View user's profile Send private message View poster's gallery Reply with quote
Just a driver



Member Since: 29 Nov 2021
Location: Norfolk
Posts: 416

United Kingdom 2009 Freelander 2 SD4 GS Auto Stornoway Grey

Have you got an old style light bulb low wattage somewhere that has not fully blown , and is touching then another time it’s not. Am no expert just a guess.

Post #445514 20th Oct 2024 9:09 am
View user's profile Send private message View poster's gallery Reply with quote
DEG5Y



Member Since: 22 Jul 2016
Location: Widnes
Posts: 162

United Kingdom 2009 Freelander 2 TD4 XS Auto Santorini Black

An RCD is looking for a current difference between the Live and the Neutral.
That current difference usually comes from a path to earth.
The fault isn't always in the Live conducter as technically the Neutral becomes Live whilst current is flowing through it. So a fault in the neutral can cause the RCD to trip.
That fault doesn't have to be a loose or 'nicked' wire as it could also just be a squashed wire, as that affects the integrity of the insulation.

The link between the two sides of the CU, whilst it should be separate, there could be a Neutral link.

You haven't said what is fed off the side that keeps tripping.
The Usual Suspects are based around water, Cookers, Washing machines, Tumblers etc

EDIT
Just realised, I've virtually repeated IM's post

Post #445521 20th Oct 2024 3:40 pm
View user's profile Send private message View poster's gallery Reply with quote
MartynB



Member Since: 08 Aug 2011
Location: Currently Rootless !
Posts: 1779

United Kingdom 2009 Freelander 2 TD4 GS Auto Zermatt Silver

I’ve recently had the split circuit RCD protected board replaced with a full RCBO unit , combined MCB/ RCD breakers . It seems a much more practical solution . You only lose the one faulty circuit rather than multiple , and at that point it’s already an indication of that circuit needing attention one way or another . . If you have to call out a sparky to sort out your current problem it won’t be that much of an addition to get the board swapped out for RCBOs 2009 GS Auto Zermatt Silver - Sold June 21 after 10 years of ownership

2016 Subaru Outback SE 2.0 diesel SE Premium Lineartronic Sold 2024 after 8 years and 80k miles . Best Car I ever owned !

2023 Toyota Hilux invincible X 2.8 Auto .

Post #445527 20th Oct 2024 6:32 pm
View user's profile Send private message View poster's gallery Reply with quote
O-B-Wan003



Member Since: 12 Sep 2017
Location: county Down
Posts: 125

United Kingdom 2014 Freelander 2 SD4 HSE Auto Santorini Black

Jules I'd start by turning everything off and adding a circuit one at a time if that's possible. It could simply be a loose earth causing the trip or a faulty appliance tripping. My last trip was the time switch on the cooker which tripped everything and a faulty cheap Chinese oven bulb that kept tripping my mother's house.

Sometimes it's the simplest of things that cause the biggest heartache.

Stephen.

Post #445529 20th Oct 2024 8:31 pm
View user's profile Send private message View poster's gallery Reply with quote
jules



Member Since: 13 Dec 2007
Location: The Wilds of Warwickshire
Posts: 4998

United Kingdom 2014 Freelander 2 SD4 SE Auto Firenze Red

Ive now got all the freezers protected on a circuit from Bank 2 - which has never tripped - So I can live with that until the electrician comes.


Ian - Yes I do have external outdoor circuits - to the 2 greenhouses, sewage treatment plant (which runs continuosly), pond pump and a couple of sockets but they are all the Bank2 which doesnt trip.
And we've not had the central heating running yet, except for 1 hr at 0630) - All the CH electrics are on Bank 2.

Today RCD 1 started tripping occassionally from 10am and then every few mins from around lunchtime, but this evening hasnt tripped at all.

Yesterday switching on the induction hob triggered the trip even though the hob is on the other Bank (2). Today switching the hob didnt triggger it even though it was triggering "by itself".

Im out of ideas - I'll wait to see what the sparks says, but I can see swapping the board for one with RCBOs would help narrow down the cause.
Its difficult to switch off circuits and wait to see if it triggers when 1) triggering is so variable 2) the family want to use things. I 'll have a better chance of isolating things during the week. Jules


Last edited by jules on 20th Oct 2024 11:41 pm. Edited 1 time in total

Post #445532 20th Oct 2024 11:27 pm
View user's profile Send private message View poster's gallery Reply with quote
jules



Member Since: 13 Dec 2007
Location: The Wilds of Warwickshire
Posts: 4998

United Kingdom 2014 Freelander 2 SD4 SE Auto Firenze Red

DEG5Y wrote:


You haven't said what is fed off the side that keeps tripping.


Laundry - ring - dishwasher, washing machine , tumble dryer, water heater
Garage - ring - sockets (7x double), 2 freezers, garage doors, pond pump, carport (lights & sockets), flood lights
Lights - landing, bedroom x2, bathroom x2, front hall
Kitchen - fridge/freezer + sockets (not cooker or central heating)
Lights - kitchen Jules

Post #445533 20th Oct 2024 11:37 pm
View user's profile Send private message View poster's gallery Reply with quote
DEG5Y



Member Since: 22 Jul 2016
Location: Widnes
Posts: 162

United Kingdom 2009 Freelander 2 TD4 XS Auto Santorini Black

Lighting circuits are not usually the problem, but if you can do without them through the day while you proove things turn them off. (With so many 'Chinese' imported metal light fittings and modern LED bulbs, it could be this cicuit!)
If it still trips, put it back on and move on.
If you can do without the Laundry circuit for a day, turn that off.
Again if it trips move on.
Apart from the pond pump you could turn off the garage circuit as long as your not in and out of the freezers they should be OK. Can you run a temporary feed to the pump from the otherside of the board?
Fianlly the kitchen.

Have you not been able to identify what appliances are running when it trips?

Don't just turn off, actually unplug anything you can do without.
Unplug because most things are single pole isolation which means there is still a path through the neutral. Should you have an imbalance on the neutral you can still cause a RCD to trip on a dead circuit, if your earth and neutral touch.

Does it trip more when it's raining?

Like I said before anything associated with water is on the suspect list but also anything that has a heating element.

ps.
I'm intrigued by the number of freezers. It's either to make a 'White Walker' feel at home, or the population of your local area is getting smaller and you buy a new freezer everytime someone goes missing!!!

Post #445535 21st Oct 2024 6:33 am
View user's profile Send private message View poster's gallery Reply with quote
jules



Member Since: 13 Dec 2007
Location: The Wilds of Warwickshire
Posts: 4998

United Kingdom 2014 Freelander 2 SD4 SE Auto Firenze Red

Thanks Degsy

Don't just turn off, actually unplug anything you can do without.
Unplug because most things are single pole isolation which means there is still a path through the neutral. Should you have an imbalance on the neutral you can still cause a RCD to trip on a dead circuit, if your earth and neutral touch.

Yeah it took me a few hours of thinking to realise I needed to physically remove appliances as they have only a single pole switch.


Does it trip more when it's raining?
Definitely YES but its variable

Like I said before anything associated with water is on the suspect list but also anything that has a heating element.
Today Im going around disconnecting everything not essential

ps.
I'm intrigued by the number of freezers. It's either to make a 'White Walker' feel at home, or the population of your local area is getting smaller and you buy a new freezer everytime someone goes missing!!!
Haha We just grow a lot of vegetables and fruit - rarely need to buy them from shops and tend to buy meat in bulk from a local butcher. Jules

Post #445537 21st Oct 2024 8:56 am
View user's profile Send private message View poster's gallery Reply with quote
DEG5Y



Member Since: 22 Jul 2016
Location: Widnes
Posts: 162

United Kingdom 2009 Freelander 2 TD4 XS Auto Santorini Black

"Does it trip more when it's raining?"

"Definitely YES but its variable"


Could be pointing towards an external circuit.
If a circuit gets wet during the rain, it could take a while to dry out and therefore continue tripping.


Carport (lights & sockets) - How good is the IP rating (is the instalation good enough to maintain a high IP rating?), is the atmosphere damp?

Flood lights - Are they permanently on? Do they rely on a light sensor?

Just a few things to think about.

Post #445538 21st Oct 2024 9:18 am
View user's profile Send private message View poster's gallery Reply with quote
IanMetro



Member Since: 11 Sep 2017
Location: Somerset BS21
Posts: 3126

United Kingdom 2014 Freelander 2 SD4 Metropolis LE Auto Fuji White

MartynB wrote:
I’ve recently had the split circuit RCD protected board replaced with a full RCBO unit , combined MCB/ RCD breakers . It seems a much more practical solution . You only lose the one faulty circuit rather than multiple , and at that point it’s already an indication of that circuit needing attention one way or another . . If you have to call out a sparky to sort out your current problem it won’t be that much of an addition to get the board swapped out for RCBOs


This seems to be the best advice.

When I get trouble, mainly in external garden and workshop circuits, I often wonder whether I should start all over again with fresh wiring around the house and to the external feed. Now I know about individual RCBOs it makes sense, but rewiring would be very expensive and inconvenient. FL2 XS SD4 Auto 2010 2012-2017 (21k - 91k miles) (MY2011)
FL2 Metropolis SD4 Auto 2014 2017- (16k - 77k+ miles) (MY2015)
Metro in its 11th Year of (Extended) LR Warranty / Full LR Service History
(Expensive, but Trouble/Worry free - hopefully?)

Post #445539 21st Oct 2024 9:34 am
View user's profile Send private message View poster's gallery Reply with quote
jules



Member Since: 13 Dec 2007
Location: The Wilds of Warwickshire
Posts: 4998

United Kingdom 2014 Freelander 2 SD4 SE Auto Firenze Red

After checking everything in the garage and found no faults I started checking the external sockets and switches today.

In the 2nd box that I opened (feeding power to the sewage treatment plant) I found a broken neutral connector. The wire just fell out of the split brass connector when I took the face plate off.
The STP was still working though.


Click image to enlarge



Hopefully that is the cause of the tripping. The tripping has ceased anyway since its started to dry up outside. Just need to wait for some more heavy rain to test my theory.

But Im definitely thinking about RCBOs. Jules

Post #445545 21st Oct 2024 4:44 pm
View user's profile Send private message View poster's gallery Reply with quote
Post Reply  Back to top
Page 1 of 2 12>
All times are GMT

Jump to  
Previous Topic | Next Topic >
Posting Rules
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum



Site Copyright © 2006-2024 Futuranet Ltd & Martin Lewis
Freel2.com RSS Feed - All Forums


Switch to Mobile site